A couple of things.
1) This IS a single-phase motor and not a three-phase one, right ?
(don't connect a three-phase motor to a single supply)
2) The 13A fuse in the plug is designed NOT to blow unless the current exceeds 50% more than it's rating, which means it won't blow until 20A in the steady state (see
https://www.pat-testing-training.net/articles/fuse-operation-characteristics.php) - and it will handle significantly more current for a while. As long as the motor reaches its full speed within a second or two the fuse will probably take the inrush current.
3) on breaker classes. The breaker in the mains wiring is intended to protect the
wiring, not the appliances connected to it. As thikone mentions above, class B will take up to 5 times (actually between 3 and 5 times) the current rating -
for 10 seconds - so if your breaker is a 20A one it should handle 60-100A during startup. Given the motor nominal current of 8.5A that's probably fine. You
could change to class C, which will take between 5 and 10 times the current, but that's only for one second.
4) with all this you're not protecting the motor. It's designed to draw 8.5A so if it takes more, there's a problem, and neither the fuse in the plug nor the breaker will prevent that. This is why you'll eventually need a thermal overload set to 8.5A (or slightly above).
But for a quick test, if it's single phase it should work, just check before you try it that it's running free and is earthed and you can switch it off quick if it doesn't start running quickly (which might indicate a problem with the starting mechanism) - or if there's smoke of course ...