Yes it is in the hands of a professional at the moment, assessing what's afoot.You need to get the motor checked by someone who knows about motors, but not worth getting it rewound so might just be as easy to get a new motor.
I hope you measured the loop impedances to ensure the wiring can take the higher current during a fault condition, type B needs 3 to 5 times rated current to disconnect whilst a type C needs 5 to 10 times rated current which means a 16 amp device might require 160 amps compared to 80 amps for the type B. Having seen the results where people just change a protective device it is always an eye opener, no different to wrapping a fuse in foil. Changing any protective device is a change in original design and therefore should only be done by a qualified sparky with the right test equipment who can provide a certificate of safety.
I didn't personally measure the Ze and the R1 +R2 of lighting circuit as I am neither an electrician, nor have the appropriate test equipment. However, this was carried out by the electrician who had initially suggested the solution.