Prior to the changes in 2008 the lighting circuit would not have required RCD protection but since I intend to surface mount all cables and fittings then all the circuits will need RCD protection as they will not be protected against mechanical damage.
I believe you are referring to regulations 522.6.6, 522.6.7 and 522.6.8 - these apply to cables which are
concealed - if the cable is clipped to the surface of the wall along the entire length of the circuit and is not concealed then they do not apply. That said there may be other regulations which would apply and require an RCD to be fitted.
The wiring regs require that cables are installed to minimise the risk of mechanical damage (522.6.1, 522.6.2) and if the wiring is at risk of medium or high severity impacts then protection is required by choosing a wiring system with suitable mechanical properties, a suitable/safe route, providing mechanical protection etc.