So last night the fuse blew on my workshop, taking the dining room lights with it, long story short, after much messing about up a ladder tracing the cables I discovered the issue...
At some point prior to my ownership (likely during the current kitchen being fitted) the original 10mm² SWA installation was cut off at the wall of the house, and mated crudely with some electrical flex, which then plugs into a 13A RCD socket inside some boxing in, which is shared with the dining room lights, and alarmingly attached to a 60A Fuse (not MCB) in the consumer unit with 1.5mm² Twin and Earth.
Now the fact I had a 60A feed and consumer unit, which had been properly installed (and had building control certs) was a genuine selling point... Whereas what I've found seems like an unnecessary and frankly dangerous cludge.
My planned resolution is to:
(I'll say right now that whilst I know I'm capable of doing all the work to a good standard, I am not formally a "competent person" in a domestic setting; though as far as I can interpret this would not be adding new circuits or otherwise doing Part-P/notifiable works.)
At some point prior to my ownership (likely during the current kitchen being fitted) the original 10mm² SWA installation was cut off at the wall of the house, and mated crudely with some electrical flex, which then plugs into a 13A RCD socket inside some boxing in, which is shared with the dining room lights, and alarmingly attached to a 60A Fuse (not MCB) in the consumer unit with 1.5mm² Twin and Earth.
Now the fact I had a 60A feed and consumer unit, which had been properly installed (and had building control certs) was a genuine selling point... Whereas what I've found seems like an unnecessary and frankly dangerous cludge.
My planned resolution is to:
- Replace the 13A socket with an junction box feeding the dining room lights only and use the existing cable run to join this onto the existing downstairs lighting circuit (which has capacity to take the load)
- Then add an IP68 junction box where the existing SWA was truncated, so I can run new SWA clipped direct to the outside wall and into my meter cupboard connecting to a
suitable isolator (I have several metal 63A isolators spare).It has been pointed out to me that for wiring protection a 60A fused switch or MCB would be necessary, this was my original thinking, but whilst posting I got isolator in my head as it's what I'm used to attaching glands for SWA to. - Connect that
isolatorMCB directly into the tails as they leave the 100A RCD that protects the Consumer Unit for the house. - Pull the now unused 60A fuse in the consumer unit and leave it disconnected.
(I'll say right now that whilst I know I'm capable of doing all the work to a good standard, I am not formally a "competent person" in a domestic setting; though as far as I can interpret this would not be adding new circuits or otherwise doing Part-P/notifiable works.)
Last edited: