You have highlighted one of the issues with the ring, it only takes a break in one of the wires and you now have a 2.5mm cable protected by a 32 amp device.
For that you really needed singles in trunking and conduit drops, with a radial you get to the last socket and that's it, with a ring you now have to get a cable back to the board.
The other issue is the time it can take to fully test a ring main, if someone has been playing and bridged the ring with another socket some where it can be a right nightmare to find and I have seen a few.
The ring main harks back to the post war years and copper shortages, the original concept was the ring only provided power to supply a kettle and two electric heaters because that is all they thought the house holder needed, there was a radial to a cooker and one lighting circuit for the whole house.
That concept did not change for decades except we used a ring upstairs and a ring downstairs whilst spliting the lighting the same and all from a single RCD board. The big changes have come about because of our demand for more and more electrical appliances and our increased awareness of safety, now we have to put a lot more time into the design of an installation and with far more circuits, 18 and 27 way distribution boards being readily available.