Now you've gone past my knowledgematt":3rygrtmo said:Did you check the zone valve, if fitted, for this particular part of the circuit?
Zone valve you say?
Now you've gone past my knowledgematt":3rygrtmo said:Did you check the zone valve, if fitted, for this particular part of the circuit?
Yep, it is not far above the pump but I'm at work so can;t see it right now and can't remember where it is in the line.RogerS":3ia5q4v7 said:Do you know where it is located? Do you have access to it?
Things to check are ..
1) is it getting volts to turn it on
2) if it is then is it actually turning on.
The zone valves that I have feature a manual override. You can move this by hand and latch it in position. If it is getting electricity and has been enabled then this manual override will probably be very easy to move. That's probably one of the easiest ways to test for (1) and (2).
Is it a zone valve (ie on or off to one zone) or a diverter valve (ie routes ch water to either this zone or that zone)?
TrimTheKing":2hrnffsf said:Yep, it is not far above the pump but I'm at work so can;t see it right now and can't remember where it is in the line.RogerS":2hrnffsf said:Do you know where it is located? Do you have access to it?
Things to check are ..
1) is it getting volts to turn it on
2) if it is then is it actually turning on.
The zone valves that I have feature a manual override. You can move this by hand and latch it in position. If it is getting electricity and has been enabled then this manual override will probably be very easy to move. That's probably one of the easiest ways to test for (1) and (2).
Is it a zone valve (ie on or off to one zone) or a diverter valve (ie routes ch water to either this zone or that zone)?
Will be home around 19:00 tomorrow so after I've bathed and put baby to bed I will take a pic and post it up to help.
I know the 'latch' you are talking about, kind of spring loaded thing that 'relaxes' when it is on? That seems to be working okay as I checked that yesterday and when the heating was set to off you can still move it but it's very stiff and you can hear/feel the valve moving, but when the hearing's on it is slack and moves side to side easily.
22mm (I think, haven;t measured it but from memory) copper from the boiler, rad flow/return legs are 12 or 15mm.head clansman":1guqwf3m said:hi
out of interest what internal size bore pipe has your system got ? is it by chance micro bore , any chance whilst sweating a new joint on the pipe it is now blocked with solder , turn on the heating and place hands either side of the replaced joint to test temperature .hc
TrimTheKing":34sehins said:Evening all
.......
Heating is now fired up and the downstairs underfloor heating is toasty again, the bathroom towel rails are boiling ......
Sorry my bad. It's getting past the pump to the underfloor (which goes horizontally) so it's actually flowing through the pump, but doesn't appear to be climbing the pipe to upstairs.Jake":auu9e7ej said:Haven't read the whole thread, mea culpa. That seems to be slightly in conflict with what was just said about it not getting past the pump.
Yep, the system runs UF, upstairs towelrails/Megaflow and upstairs rads.Jake":3vo1xrit said:Can you isolate the UF and if so does that change anything?
Thanks RogerRogerS":2mcjdfxf said:I think we need to clear the decks and go back to first principles.
It is a pressurised system.
Looks as if there is an air-lock somehwre stopping three rads from heating up.
How about this for a suggestion?
Turn off the lockshields and TRVs on the 3 rads.
Turn off the TRVs on the remaining rads and also switch off if poss the feed to the UFH. Basically we're trying to separate the system into two halves. NB Do you have a balancing valve in the system...ie a valve/whatever between flow and return that acts as a shunt if/when all the TRVs are closed?
(X) Undo bleed valve on rad 1. It should yield some water which is the water from rad 1 coming out under the pressure in that rad. Not much should come out. It should gradually diminish in volume and flow as the pressure drops.
Once it has stopped open up the lockshield on that rad. Water should start to come out again which is due to the pressure in that leg of the ciurcuit. Quite a bit will come out. It should stop once the pressure has been released.
Once it has stopped I'd re-pressurise and while keeping this bleed valve open the water should start to flow again. Let if flow for quite a while and in an ideal world it will stop and air will come out which is from your airlock and then water. If that happens then close the bleed valve, re-pressurise the system, open up your lockshields and TRVs on rads 1 to 3 and turn on the pump and zone valve so that just these three rads are in the circulating loop. Hopefully they should warm up.
If you don't get to the stage of water-air-water on rad 1 then close the bleed valve and the lock shield. re-pressurise and this time open the TRV on rad 1 and then the bleed valve and see if you get the water-air-water sequence.
If you don't then close off the bleed valve on rad 1, close the TRV and repeat with rad 2 from (X) above.
I think it should work.
TrimTheKing":i4pkopft said:I guess I should be adding some more inhibitor. How do I do that???