I'll stand corrected (or sitting at the computer) if wrong but I was taught to never use a coiled cord as it increases the resistance creating heat in the wire coils. Either pull all the cable out of the reel or get a shorter cord instead.

Pete
Sorta right- it increases the APPARENT resistance (inductive reactance actually) as it is a 'loosely coupled coil'

https://en.wikipedia.org/wiki/Electrical_reactance - look down towards the bottom for inductive reactance...

The higher the current, the more the reactance- and the hotter it gets...
And yes- it certainly does create heat...
1729194188226.png

1729194226105.png

1729194368164.png
 
Last edited:
Flex doesn't mean something is not part of the fixed installation.
Another way to interpret this is that fixed wiring has no movement, it cannot induce any strain into the conductors especially the CPC. Using a flexable cable makes sense in many applications where you are connecting from something fixed to something that has some movement and in cases like the hand dryers there is no reason to use the flex, it could easily be done in PVC conduit or mini trunking but the OEM decided otherwise. Once a cable is flexable you can have issues where many strands of the CPC might have broken due to the flex and cable gland but it would still bell out as continous, now the PAT test would test by passing a current through it which can cause it to just blow and become open circuit which is what could happen under a fault synario that could leave the appliance in a dangerous state, ie live metalwork.
 
Sorta right- it increases the APPARENT resistance (inductive reactance actually) as it is a 'loosely coupled coil'

https://en.wikipedia.org/wiki/Electrical_reactance - look down towards the bottom for inductive reactance...

The higher the current, the more the reactance- and the hotter it gets...
And yes- it certainly does create heat...
View attachment 190450
View attachment 190451
View attachment 190452

My understanding on this is because it's carrying AC current - it's acts kind of like an electromagnet (although without an iron core), and induces it's own reactive current every time the current reverses - hence "inductive reactance".
 
Yep, coiled can get warm, stretched out, not so much.
I did it once myself without thinking. Just a dumb moment.
Plugged an electric heater into a mostly coiled cable reel and 15 or 20 minutes later realised that I'd done something stupid.
When I unspooled the cable the bulk of the flex from inside the coil was too hot to touch and super floppy.

To do some numbers:
In the UK you can buy a 50m extension cable, good commercial brands, no problem.
That is 100m live and neutral return.
In 2.5mm sq extra heavy flex the wire has a resistance of 0.74 ohms
Carrying its rated load of 13A from a standard plug, the cable drops 9.6V along the wire and dissipates 125W (V=IR, Power = IV = I squared R = V squared/R)
Remember the heat put out by an old style 125W lightbulb. Not so much spread out along 50 metres but imagine all that heat trapped inside the coil of wire. It will get very hot very quickly.

Do the same for a lightweight cable reel, same length but 1.5mm square and 10 amp rated (though it will be on a 13A fused plug so relying entirely on the user not to overload it)
Now we have 1.21 Ohms resistance, 12.1V dropped along the cable and almost the same heating, 121 W even though the current is less. Again the cable will quickly get hot if coiled up.

Electric heaters are the killer.
Most of our tools only run for a short time. Anything that runs continually at high power for a long time poses the greatest risk of heating and fire.
We should teach ourselves to be nervous of electric heaters, immersion heaters, and to a lesser degree powerful pump and fan motors because these are big loads that can be left running for hours at a time.


Oh, and this is why the way a cable is installed must be taken into account when you design household wiring.
These dissipation numbers aren't much different for fixed wires, so you could easily have 125W of heat being generated in a long run of twin and earth. No big deal if that wire is in free air to cool it, but buried under 6 inches of loft insulation a wire can become noticeably warm even if it is stretched out and not concentrated on a reel.
 