Hi all, looking for information on solar panels.
We have a 4kW solar panel system which was installed about 13 years ago and so qualifies for FIT payments. I would like to add more panels now, which will not qualify for FIT payments, plus battery storage. I don't want to jeopardise my entitlement to FITs as they are worth around £3000 a year overall now. Is it possible to have another 4kW system alongside the existing one without major issues? Could a battery be used to store energy from both sets of panels? Could both sets of panels be integraded into the existing house mains? I have contacted my DNO and they said I could expand my system without problems.
Any advice would be appreciated.
K
You will really have to look at what your current FIT contract terms are- many won't allow any export modifications at all!!!! (if modified, then you may lose your 'grandfather' status on the original setup... and its current payment levels...)
As you are looking at a battery and new hybrid inverter anyway, a way around that is to leave the existing system as is, and simply have a parallel NON-export hybrid (most can be set up like this in the menus) and have your house loads on the hybrids output, with a feed from the meterbox tails to the hybrids mains inputs...
Set up correctly, you will get zero export from the hybrid (so not affecting your FIT original system in any way) and the house loads will run off the hybrid and its battery pack, unless the battery goes flat, in which case it will 'fall back' to the mains input connection ie the house loads connect back to the grid as they currently do...
With the battery bank set to charge from solar only, this will minimise or even zero the grid usage (with correct battery bank capacity and panel wattage calculated to handle your 'normal' household loads)- you may use a smaller hybrid/battery bank and only have 'some' of the house circuits on its output, with other larger loads still staying on the mains grid instead- doing it this way allows almost unlimited rearrangement to suit anyone's budget/requirements...
You won't be able to use the existing FIT system during blackouts obviously, but you will have the hybrid system running the house when all your neighbours are lighting candles lol plus as your mains grid usage can be reduced/zero'd, the FIT system becomes purely a money making exercise...
(this is a hybrid inverter- actually my 12kw one here (being used offgrid) and it shows the mains in (from the meterbox tails via a suitably rated breaker, mains out (which feeds some/all of your household circuits ie feeds your consumer unit) the PV 1 and 2 (mine can handle 3kw of panels on each PV input) and the battery terminals (48v in mine)- they come in a wide variety of inverter wattages, battery voltages and solar wattage limits (plus you can always add more battery capacity or more solar panels simply by adding external MPPT charge controllers with their own arrays attached directly to the battery bank...)
Obviously LFP lithiums are the best choice (L/A can be used, but they really are a bad choice these days) and can be either individual cells like mine or a 'component box' (BYD for example make their 48v range of 'powerwalls' as do several other brands) and hybrid inverters contain their own inbuilt ATS (automatic transfer switch) as well...
My 20kwh battery bank (15x 400Ah single cells- wired in series for 48v nominal)
BYD 48v 'battery in a box' thats it sitting on the floor (not mine lol)- most brands are 'modular' and you can increase the capacity simply by 'stacking another drawer'... good for those that want a simple 'plug and play' system where everything is in the one box...
Best part is that you can literally have the entire system isolated from the grid for those places that dont allow export solar at all- just use a standard external ATS wired up as a 'backup genny switch', but running in reverse ie the primary source is the hybrid rather than the grid connection, and the mains grid is connected to the 'backup generator' connections when wiring it in- the hybrid will run the house loads until it hits its programmed lower battery limit and then shuts down, and only then do the house loads 'fall back' on the 'emergency generator' aka the mains grid... Set up like this, the hybrids solar ONLY does its own battery bank, it has ZERO export at all (for those that aren't allowed solar exports) and the whole system is classified as an 'external generator' to all intents and purposes (meaning that non 'gridtie inverters' can be legally used- as they are NEVER connected to the grid...)
(that shows a three phase supply, but single phase ones are readily available as well)