Switching Single phase To 3 Phase

UKworkshop.co.uk

Help Support UKworkshop.co.uk:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Delaney

Established Member
Joined
4 Jul 2023
Messages
268
Reaction score
116
Location
Hampshire
Looking to move workshops.
I currently run 3 phase motors (not sure as of writing if VFD compatible).

I’ve got a couple Felder machines. All 2022 models.

FB710 bandsaw
AD410 planer
k700 panel saw
SCM DMC 90 wide belt sander
Extractor

The workshop I’m visiting today does not have 3 phase, so am exploring possibilities to be able to use single phase.

My motors are rated 3 phase 400v. The machine that takes the most power is the sander. I think around 7kw when operating, as it has two motors.

I would be interested in hearing peoples experience and tips to do so. I assume VFD’s are the most common way to convert?

Many Thanks.
 
The VF in VFD is 'variable frequency'. Its main claim to fame is that is gives variable speed. The VFD device is a sophisticated control computer for the motor; it has all sorts of protective (overload) capability and can do things like soft start and braked stop.

If you have been using the machines plugged directly into a 415v three phase outlet, most of these capabilities are not required.

In your case, a traditional rotary converter (Transwave are about the best-known manufacturer) might be a better fit. MT7 or MT11 here: https://transwave.co.uk/Rotary-Converters

You would need to ensure the incoming supply and distribution board can accommodate the rotary converter, which might need some rewiring (MT7 needs 40A breaker and MT11 needs 60A breaker).

It is not clear if your extractor is single or three phase. If it runs when the sander is running and is three phase, you have to add its demand to that of the sander. If it is single phase, the single phase supply needs enough capacity for rotary converter plus extractor.

Edit: if you read this before your visit, take a good look at the incoming supply (and fuse rating) to the premises. Perhaps take a photo and post it here. If the wire coming in looks like a drinking straw, there may be challenges; if it looks as thick as your arm, it will be OK.
 
The main 'problem' with VFDs is that you need to wire them direct to the motor, on older simple machines with a switch and a motor this is no big issue on more modern machines with micro safety switches etc it can all become a real faff to keep it working the same. Also your machines are probably still going to be valuable on the second hand market in 20years, messing about with the electrics and a VFD will likely impact any future resale value. A solution that serves all the machines a three phase supply so that you just plug and play would be an awful lot simpler. at MrLatte has said a rotary converter would suit this.
 
Firstly I would always ask about cost to bring 3 phase to the workshop - it can vary hugely but sometimes it's worth it.

Agree with others - for your modern machines it'll be better to get 3 phase to them than to wire in VFDs to all of them. Are rotary converters still state of the art?
 
Are rotary converters still state of the art?

They are proven, simple, robust technology.

For a plug and play situation, where you are plugging into 230v single phase and playing with 415v three phase on multiple machines, there are very limited other options (Drives Direct, JFK Electrical, various Chinese offerings). It is a bit of a niche market.

Things are different if it were a single machine - that is where an individual 220v three phase output VFD would be more economic. With 4-5 machines as the OP, the rotary converter machine and wiring cost (amounting to a 40A or 60A breaker, cable and isolator, by any standard electrician) can effectively be divided up between them and there is zero labour/reconfiguration on the machine (the reconfiguration would need an industrial control engineer, less easy to find and a lot more expensive in itself; reconfiguration required on every machine).
 
Like you, I’ve just moved from a 3ph to 1ph workshop with several 3ph machines.

One VFD/machine option was out due to expense and faff.

“Digital phase converters” are often just VFDs, unless you go for a very expensive pure sine type. You need to buy a much bigger one than the largest motor you have.

Picked up a 10hp rotary phase converter secondhand. Other than a bit of noise, the extra few seconds it takes to turn on and off, and slightly slower spin-up times, it’s like having normal three phase.

Hardly any circuitry, and easy to replace components, so it’s got the robustness of electromechanical things. Compare with solid state power devices.
 
This should do it:

20201118_133720_resized.jpg


https://www.jfkelectricalni.com/product/digital-phase-converter-11kw-15hp-240v-in-400v-out/

No affiliation but two friends have bought from him and the units, though not more than a couple of years old, are working fine.

Don't cheap out.
Get a size bigger than you think you could get away with and you will run the device comfortably inside it's performance envelope. Components will be less stressed, wil run cooler and this should increase the lifetime and long term reliability of the drive.

On a DPC like this, the largest single motor that it can start is 60% (I forget, you need to check) of the rated power.
 
Last edited: