Minor one. If you have a fire, an investigator found your setup, it would probably negate your insurance.I have a welder with a short 13A to 16 A extension lead. The 13 A plug has a 15 A fuse wire in it as Doug said above. While I couldn't recommend this from a safety point of view it does work and for short periods and no other big loads on the ring at the same time I can't see a problem.
I don't think you need 25A fuse, but defenitely it should be 'C' type protection. In fact, even even 13A with 'C' curve might be enough.and make sure your fuse box has at least a 25amp `C` or `D` type protection'
Thats what I was on about, the C type breaker. Thanks for the correct term.I don't think you need 25A fuse, but defenitely it should be 'C' type protection. In fact, even even 13A with 'C' curve might be enough.
So many times I see in comments to install 16A or 25A fuse while the load will only draw high current for a short period of time and while running will probably never exceed 10A. What you need is delayed reaction that is denoted by a letter B, C, D. Usually, in residential area type B is installed.
My Felder machines came with the manual that stated to use C 16A breaker. Works fine even with 4kW three-phase motor. After short startup it doesn't consume a lot, much less that 4kW, even under moderate load.
I also have spot welding thing from China. It was tripping B 13A breaker, but works fine with C 16A but doesn't work even with B 25A.
The beauty of changing from B to C is that it would still trip with continues current exceeding rated current 13A or 16A, but will allow for short spike of current that is too short to damage the wires it protects.
Many thanks for that explanation and examples, really useful information and much appriciated,I don't think you need 25A fuse, but defenitely it should be 'C' type protection. In fact, even even 13A with 'C' curve might be enough.
Ask permission if you have to from the landlord then get a qualified electrician to look at the installation and advise.So what would you advise is the correct solution to the problem the OP is having.