Tolerance on pile positions is normally 75mm. They like like they are slightly more than that but would most likely pass a design check.Looking at the white rectangle it looks like one of the piles will not be completely under the ground beam. Is this acceptable?
it would be good to expand the ground beam locally around the pile with a few L bars to tie the concrete into the rest of the beam.
@marcus one thing that does concern me was how was the top of the piles treated. Is that the as cast top of the piles. Was the top few hundred mm broken off to remove the crude that floated up in the pile.