I am about to buy a compressor and the manufacturer says I can’t use an extension lead. It needs a 16a supply which I have for my planer/thicknesser. The P/T runs through an extension lead of about 2m. Why can I not use an extension lead for the compressor? What about just removing the existing power cable and replacing it with a longer one? Also what is the longest air hose I can use with a compressor before I get power loss etc? It is 3hp/14cfm/150psi. Thank you
My advice is that if you want to use a longer cable the first thing to do is check the size of the conductors. They are likely to be 1mm or 1.5mm just possibly 2.5mm, if they are not 2.5mm sq then you can easily swap the original for 2.5mm sq and make it a 10m cable, possibly longer.
The reason for not allowing an extension cable is that the vast majority of extensions are 1mm or 1.5mm and may well be copper coated steel or aluminium, these extensions even if copper will have the resistance that
@Sideways is talking about.
With the power supply as mentioned the 16A is certainly better as it has capacity beyond the normal 13A. however the 13A is quite capable of supplying the power required. The important point is that the MCB or RCBO has the correct curve for a motor to start so you need (or are best advised) to have a circuit with a type C or K breaker, the majority of circuits use a type B.
The type B allows a 3~5 times inrush current so it’s quite possible that your air compressor will pull enough to trip one on startup
The type C allows a 5~10 times inrush current so is useful for things like motors that usually go over the type B limits
The type K allows a 8~12 times inrush current so is useful particularly useful for motors.
However there are calculations required for the circuit to ensure that you are able to safely change the MCB type so this is a job for a competent electrician and you may need to run a dedicated circuit.
With the longest air hose you can run, this is very dependent on the use you intend. I have used a 50 meter set of extensions to run an air duster, however for my spray setup I run an 8 meter 13mm feed to close to the paint room this has 2 filters on it to try to ensure its clean dry air
then I use a 6mm or 8mm from that to the gun. So far I’ve mainly used water based or oil finishes so the 6mm has been easily capable of supplying the required volume.
I recently got a gun with a 4mm tip to spray household vinyl paint, that may require the 8mm hose. And while I know that going airless is the best for that material I can’t justify spending the £3,000+ for the little use I will get out of it, so I will continue to use an air gun.
I live in a climate that kills the cheaper air hoses in a couple of years so have had to switch to reinforced hoses, the most flexible ones will have double or more the life of the cheap ones.