Are you there Myfordman?

I need some advice wiring up a large motor, as per pictures it's 3 phase and has been star connected in the past.

My main concern is the best way of switching it, do you think a DOL 415v starter fitted with a 13.0>18.0 Amp overload be OK?

P6250763 (640x637).jpg


P6250767 (640x370).jpg


If it helps it's a rotary vane vacuum pump so apart from it's own momentum it won't be starting on load.

Thanks for your help.
 

Attachments

  • P6250763 (640x637).jpg
    P6250763 (640x637).jpg
    216.5 KB
  • P6250767 (640x370).jpg
    P6250767 (640x370).jpg
    160.7 KB
Yes your proposed starter should be fine. Set the overload to 15.5 amps and be prepared to edge it up by maybe 10% if it trips.

I can see no point in retaining the snubber devices. it is possible that in a past life it was run from an inverter and someone was trying to implement a crude filter.
 
Chrispy":liub7miw said:
Excellent thanks for that advice I can now get the right bits for the job.

No problem. I fit a lot of the toolstation DOL starters on jobs. Reliable, sensibly priced and free delivery.

Other brands are available as they say....
 