Hi,
We had a UPS delivered at work, they knew the weight and got the mechanical engineering department to work out it the computer room floor would stand the weight which they said it would.
But they forgot that the removable floor tiles are only supported at the corners so when they slid it in the tiles broke!
It’s the point loading you will have to watch out for not the total weight, it’s the old thing about an elephant and a woman in stilettos standing on tarmac the woman sinks in, because the point loading on the heels is greater than the elephants weight spread over the area of its feet.
Pete