Do you actually measure it somehow? I can disconnect it but still scary to stick Ohmmeter there. Or maybe test it with short circute?
A proper multifunction installation tester can apply a controlled load directly between live and neutral and live and earth at the main isolator switch. It measures the loop impedances of the supply directly as well as calculating Potential Fault and Potential Earth Fault Currents which will be hundreds of Amps.
The local portion of the loop impedance is measured with the supply isolated using a low impedance ohmmeter that reads accurately down to 0.05 Ohms or better.
Circuit by circuit you add them up and do the maths for both L to N and L to E.
If there's a garage distribution board, you have the additional step of checking loop impedances at the DB and then measuring circuits from there.
These aren't typical DIY measurements that can be done with a normal multimeter. Those measure at most 10A of current and don't have the resolution and accuracy to measure very small resistances. A multifunction tester or set of separate installation meters cost some hundreds £ and plenty are over £1000.
Do you test it ? Yes. Every circuit must be measured like this and written up when it's installed, and sample tested again on least a good proportion of the circuits during periodic inspections. It's part of what you pay an electrician for.
The measurements are taken to ensure that enough current will flow in case of a live-neutral short or a live-earth short, so that the breaker protecting the circuit will trip inside the required time.
Also, the impedance of the local wiring used to work out how many volts will lost across the wiring at full load. This is to ensure that the wiring meets the minimum voltage requirement.
Changing the MCB type as Spectric says changes the current needed to trip it in time, so might require thicker wiring.
T&E has a thinner Earth conductor than it's live and neutral, so it might have a low enough impedance to be safe for a LN short but it could be unsafe in case of a LE short.
Changing the breaker type invalidates all the measurements and calcs done when the circuit was installed. It's notifiable work which few people apart from those qualified to do it will know how to do properly and have the test gear to prove it.