The tube diameter does not in principle matter Miles, other than to make sure it's big enough to avoid capillary effects and no so large as to become problematical to handle. Something like 3/8 or 1/2 in bore should be fine.
A U tube manometer works as follows. Think of a a length of tube with water in it clipped to a board to form a 'U' shape. It's filled so the water comes about half way up the vertical leg, and when at rest and not connected to anything finds it's own level so that it's at exactly the same height in both legs. This is a reflection of the fact that the atmospheric pressure over each column of water is exactly the same since both legs of the tube are open to the air.
When air flows in a duct what's called the static pressure drops (i.e. the 'normal' pressure reading you would get if you stuck some sort of sensitive pressure gauge into the duct) The dynamic pressure (in effect the pressure you feel on your face in a wind) increases since the air is moving.
If you were to stick one end of your tube in the duct pointing upstream into the airflow then the dynamic pressure would act on the water column in that side of the U tube. Things like pitot tubes that measure airspeed another way do it this way, but we don't want that effect. Which means that to get a static pressure reading your tube should be placed at right angles to the flow of air.
If you do this the drop in static pressure in the duct will cause the column of water in that column of your U tube to rise by an amount proportional to the drop in pressure relative to the atmospheric pressure the other leg is exposed to. Which means the water level in the other leg will drop the same amount.
Some U tube info:
http://www.engineeringtoolbox.com/u-tub ... d_611.html
You take the pressure reading by directly measuring the difference in vertical height between the water surfaces in both tubes - pressure in duct design is commonly expressed in 'inches of water'.
Do the same at another point a known distance of straight duct upstream or downstream from this and using the difference between the two readings you can (using the right formula) calculate the air speed. You'll have to Google or find a book for this.
The U tube has to be long enough so that the water column is not sucked high enough to overflow.
As Lurker says and as in my earlier post if you want to get accurate readings of airpseed the positioning of the tube in the duct is important.
On the other hand from my reading (i've only done this in practice on pre installed measuring ports, and it was almost 30 years ago) it's not that big a deal if you are only seeking to monitor the drop in air flow in your system as the filters start to blind. Make sure you position the tube the same every time and at the centre of the duct and you should get comparable readings. Bill Pentz discuses this issue somewhere on his dust collection sysytem design website:
www.billpentz.com/woodworking/cyclone/index.htm
Water filled U tubes are not really suitable for permanent installation as the water grows all sorts of algae and stuff that bungs the tube up. Plus they can be bulky and inconvenient. Which is why you see mechanical gauges like Mr. Ed's link. Dwyer Magnahelic is pretty much the industry standard, but expensive:
www.dwyer-inst.com
The U tube is dead cheap, but i guess needs some careful study to get it working right. Don't know what the H&S people may demand....