16amp plug
JFC
30 Sep 2005
London
Is there something special about a 16 amp plug or is it just a plug with a 16 amp fuse in it :? :oops:
So i can just wire my existing workshop supply into a 16amp socket and use a 16amp machine then ? :?
I had to call an electrician to answer that :oops: I should pay more attention to these things :lol:
25amp feed .
Only competent people should do electrical work due to the obvious dangers, so if you had to ask.
The supply to the w/s should be rated greater than 16a say 30a it should be protected with a mcb as should any other circuits in the shop housed in a distribution box. 16a sockets do not have a integral fuse.
To comply with current regs the 'say'30a supply should be protected by a rcd.
Since the 16A (and other current ratings) "commando" plugs do not have an internal fuse, any 16A socket should be protected with a 16A current limit. This is because the wiring from the 16A plug to the machine will be designed to handle up to 16A, but if you simply attached a "commando" socket to a 25A supply, potentially 25A could be drawn through that one connector and the associated cables, creating an overheating risk.
It's probably best to install a separate 16A breaker in your board for each 16A socket (i.e., wire them as 'radials'). If this is impossible it might be appropriate to connect a 16A MCB to an existing ring main, and connect the socket to the outlet of that. Small breaker enclosures are available that may be suitable for this application.
The MCB will only protect against over current; an RCD only protects against earth leakage, and an RCBO protects against both but is more costly. Earth leakage - a current difference between live and neutral - is often a sign that something's gone wrong, except in the case of inverter drives where it is sometimes to be expected (or so I'm told).
Of course works like these must only be undertaken by competent electricians.
Neil