Looking to upgrade electricity supply to garage with 3 phase to power two machines about 3HP each, plus lighting and rest of house etc. Getting a quote, what ampage should I ask for?
That means they have installed a larger cable which may never be used, I would think you have the maximum power available but are prevented from using it by the digital meter, what happens if you exceed the 18Kw ? Will it automatically put you on a higher charge for the higher supply or just drop out.so I can just phone up and have the power rating increased up to 36kw in 3kw increments and the change is made remotely.
The cable from the pole in the road to the meter is 35mm sq aluminium, effectively equivalent to 25mm sq copper so in theory it would support 100 A per phase. For a domestic tariff, the maximum supply is limited to 36 kW for three phase, which is about 50 A per phase. You can go up to 18 kW for a single phase supply, which is more like 80 A, but you'd have to argue quite hard to go beyond 12 kW on single phase.That means they have installed a larger cable which may never be used, I would think you have the maximum power available but are prevented from using it by the digital meter, what happens if you exceed the 18Kw ? Will it automatically put you on a higher charge for the higher supply or just drop out.