what would be the biggest motor that size of genny could handle on a red basis......
i have genny that size n it'd be handy to know.......
That's an interesting question as I haven't played a lot with genny's to really know from experience. I've searched a few relevant posts on the IET web forum (electrical engineers), some of the big generator mfrs, and some of the smaller ones to try and get an answer that feels reasonable.
These views might give you food for thought:
On a big 200hp plus generator, advice is never to try and start a motor bigger than half it's capacity. But a smaller genny can't handle that much.
0 to 50% of capacity sounds like a typical "first" load to connect to a genny. Not many will take 100% full load applied in one hit.
Then, motor startup current is very typically 5x full load, so that suggests not connecting a motor more than 1/10 rated generator capacity.
And Spectric's point about power factor is important. Motors are magnetic, inductive things. They require reactive or imaginary power to flow in and out of them as well as real power that gets consumed. The genny has to supply the real plus reactive power which is measured in KVA not kilowatts. This reduces capacity even more.
One online calculator that seems to get copied or linked to recommended a 5.7KVA generator for a 1.5HP motor. That's just 1.1kW
So yeah, about 1/5 of your generator capacity.
Darn !
You'll probably have best luck with low inertia machines like a tablesaw than something where the motor has to accelerate a lot of extra mass.
And once the first motor is running, it may be easier to start a second one. The mechanical inertia and magnetic field stored energy in first motor will help feed the startup demand of a second motor.
Running motors isn't too big a deal, it's getting them going.
Maybe the OP would have better luck if he tried a rental 20kVA generator to see if that works better.
And paraphrasing comments between a couple of qualified engineers : Generators have much higher impedance than the mains, this means that they can't supply much more current than their rated KVA. Not only does this mean that they aren't good at supplying the startup current, they aren't good at supplying the high fault current needed to trip a circuit breaker within the short time required for safety.
So a breaker can't be trusted to work as expected when fed from a generator.
ALWAYS PROTECT THE OUTPUT OF A GENERATOR WITH AN RCD.