UPDATE:
16 Amp type C fixed the problem and now we are all good......now i just need a decent extractor for it
As you earlier asked about 'combo'....
Glossary :Combo..also known as RCDO is a combination overload breaker with integral RCD (Residual Current Device commonly known as a 'safety-switch'). The switched plug sockets on the circuit, or any circuit, are known as GPO's (general purpose outlets...commonly of course known as 'power points' ). Unswitched outlets are
not GPO's.
{Bear in mind that during start-up the saw will well overload the copper in an outlet supplying it. The outlet may eventually get heat damage (cracks, cracked switch, intermittent operation)}
It's worked out as I thought...however I have come back only to do 'heads-up' over the 'unknown' aspect remaining after your advice on 'its working'. If your electrician has read my replies he'll realise I know what I am talking about and not be reactive. After this 'I'm out of here'
I am replying to recommend that your installation be tidied up properly and not just 'it now works.' By the way, if you find it 'dropping out' again 'down the track' the likelihood is that the "C" curve breaker was on the edge of its capability and a "D" might be needed.
Did you install a "C" curve breaker
with a 30mA RCD and leave the saw as 'plug-in'? ...or is the saw circuit now separated using a "C" curve breaker
without an RCD? or with a 100mA RCD...?
If the GPO's are still on that saw circuit...or the saw is plugged in to an outlet which could be used for other purposes whether you reject that notion or not...30mA protection must be protecting it.
If no RCD of 30mA now exists on that saw-circuit I suggest as previously you can replace any existing GPO's on it using outlets with built-in RCD's ....or....
The alternative, possibly cheaper, is to separate the saw onto its own circuit (with the "C" curve breaker) and connect the saw permanently...Consider this as an industrial environment in which flexible leads can be readily damaged thus connection via a junction box and an industrial type switch using protective conduit if needed to enclose wiring...That way the saw circuit without the RCD protection cannot be used for general purposes.
Having seen injuries:
Band-saw momentum doesn't let it stop immediately on 'disconnect'....for example emergency use of a mushroom headed emergency switch. Only electric or mechanical braking can cause virtually immediate stop of rotation but that's not good enough. Be always alert when using a band-saw and don't use your fingers in line with the saw blade to push work closer to that saw.