I know this isnt woodworking but is still part of my build and I find this site really helpfull so wondered if any of you people could help.

I have armoured cable running underground to my workshop (not filled in yet) and the walls and ceiling not boarded yet either. I just bought a swann SWDVK-846804-EU 4 camera system. Im going to put one camera up on the soffit of the cannopy at the front. My question is can the cctv cable for one of the cameras be buried under ground or will it need conduit. If it needs conduit then what counduit would you reccomend. The cable is BNC type. Or should I be buying a more quality cable for this one cameras needs.

Also I wanted to lay a cat 6 or 5 (undecided still) cable into the workshop too but it would be buried next to the electric cable. Ive been told you shouldnt lay it directly next to electric cable and if so to use conduit. Is this true?

Any help would be greatly appreciated. Thanks :) (y)
 
How long are the cable runs?

The armoured mains should/must have the armouring wires grounded so I wouldn't be too concerned about interference, but I'd still separate by 5cm or so. Conduit is always good - easier to pull a replacement and less likely you'll need to.

For the coax/BNC cable the important bit is the characteristic impedance, which from memory is 50 ohm or 75 ohm depending on the exact signal - make sure you get the right one. Then it'll need to be an outdoor rated cable. Past that it doesn't make a huge difference.

For the network cable, CAT5E is sufficient for gigabit and much cheaper than CAT6. Maybe get shielded if its near the mains.

Hope that's more helpful than it is rambly.
 
In this situation conduit is your friend, I'd put 2 or 3 runs down the trench whilst it's dug, crazy not too. 25mm MDPE water pipe is cheap and readily available and one could always be repurposed for water in the future if you fancied an outside tap down there. The beauty of conduit is that you can retrofit with any cable you want if you situation changes.

Yes, the official guidance is too keep data away from mains (150mm?), certainly shouldn't be run in the same conduit but unless you're planning on running a data centre down there it won't effect the cat5e, the video cable could be effected if it's not good quality but it's unlikely. You can run video over cat5 with the appropriate baluns, check out a cctv site for parts. If the cable is in a conduit and not exposed externally then you can just use normal cable, use UV stablised if outside but doesn't need protecting.

A useful tip for running a drawstring down a conduit is to use a vacuum cleaner to pull the string through with a cork or similar on the end that's a loose fit in the conduit. Also suck some talcum powder down as it acts as a dry lubricant, then pull the cables through.
 
I have armoured cable running underground to my workshop
How long is the run, how many cores and what size?

You need to use sods law, this states that whatever you do now will become wrong in the future and therefore running a duct in which everything is run will ensure you can easily change or modify what you need in the future. Also leave some draw strings in the duct tied off so ready to draw anything through in the future. For armoured supply cables you can get the same duct as the DNO's use but I have used 4 inch underground drainage pipe (Brown) on many occasions because it is cheap and accomodating and you can get everything through it without any hassle.

Analogue CCTV using RG59 cable (75 ohms) is ok upto 500 foot, and if using high quality cable can be run with your other cables but these days I would look at a digital system. On the topic of security look for the many threads on these forums as it has been discussed a lot before and there are a lot of variables, you don't just want to end up watching the scum rob you ! The main security points are make access difficult, gravel paths and drives are good plus light, the scum like dark nooks and cranies to hide.
 
If this was my project, I would "future-proof" the site by putting PVC conduit (or suitable equivalent for your area) in the trench. In my experience, the majority of the cost for these projects is digging and filling the trench. You don't have to go overboard with this by installing multi-channel duct banks, but I would install a duct, with plenty of spare pull strings, in case you need to run more cables later. The vacuum method Richard described works well until the duct starts filling up with cables. When we use one of the spare pull strings to run an new cable, we attach a new pull string to the cable to replace the string we just used. When the duct starts to get full, we don't add new pull strings.

With one exception, all of my renovation projects that required power and communications connections between buildings included at least one 100mm diameter four-channel PVC duct with plenty of pull strings. I would rather have three empty channels than need to pull one more cable later and have to dig a new ditch.

The one project I did not do this was because the customer did not want to spend the extra $750 (on the $1.5M project) for the ducting and insisted on direct burial power and copper communications trunk cables. Less than a year later, the same customer spent over $35K to dig a new trench parallel to the first to run a direct burial fiber cable between the same buildings. Two years later, the same customer paid for another trench parallel to the other two for another direct burial communications cable. Lesson captured, but not lesson learned.

I looked at the Swann CCTV system, and the 60-foot coaxial cable for each camera also includes the power cable. If you need a longer cable, you will need to provide power for the camera. One advantage of the Swann system is the cameras do not rely on a power supply at the camera so a power loss in the observed building will not affect the camera operation. If you have to install a longer coaxial cable and power the camera from the external building, you will lose the independent power feature. One disadvantage I noticed is the cameras do not have IR illumination and rely on ambient light or the visible light from the camera for night videos. This means you will not be able to covertly observe or record anyone at your buildings at night unless you have adequate ambient light from nearby street or building lights.
 
Extra pull strings is great idea.
I forgot on my extra duct underground and having two 45° bends when tried to lay another cable it was a a real ballache, tried Hoover blow with no success, ended up attacking it from both ends with nylon fish sticks string on each and a strong neonydium magnet on each. The magnets met and held to each other, pulled string through. Pulled couple of extra strings through when put new cable in.
 
If you need to get cables or something from A to B through a duct, roof space or some other set of obstacles then look at these, https://super-rod.co.uk/#products they come in different sizes which equate to a different amount of flex from fairly rigid to almost being able to tie it in a knot and I have found them to be a really valuable asset over the years and have got me out of some really tricky situations.
 
How long are the cable runs?
Underground run probably about 4/5 meters. Total run probably no more than 15m
Then it'll need to be an outdoor rated cable
Does it need to be outdoor rated if I put it in flexible conduit and then into a through box?
25mm MDPE water pipe is cheap and readily available
I like this idea. Just checked 50m for £35 from screwfix. Should be plenty to do three runs. I may carry on the runs into the walls at that length too lol. What is the inside diamter of the 25mm mdpe water pipe though. Do you know? Thanks
Analogue CCTV using RG59 cable (75 ohms) is ok upto 500 foot, and if using high quality cable can be run with your other cables but these days I would look at a digital system
Im not sure what ohms cable this swan system comes with. Will it say in the instruction manual. I was going to run some cat5e cable anyway so would it make sense to run a cat5e along with the RG59 cable just incase I do decide to swtich to a digital system in the future. If so will the cat5e cable be ok to be ran in the same conduit as the RG59 cable? Thanks
 
thanks everyone for the replys. unfortunately i have been struck down with covid so been out of actionfor the last week. Still havent tried out my cctv to see how well it looks in the dark but will try later. Im just wondering that as I am going to run a cat5e connection into the workshop just incase would it be worth running another cat5e cable to the same place as the cctv camera just incase I do upgrade to a IP cctv system. Would the cat5e cable be ok ran in the same conduit as the RG59 analogue cable?. Thanks
 
RG59 is 75 ohm.

I'd use outdoor CAT cable - not armoured - because it stands ip better to the temperature changes.
i thought outdoor rated CAT cable would be armoured. Would you beable to reccomend a decent cat5e cable to use that will go under ground inside conduit then please. Cheaper the better but still want decent. Im looking on a website called cable monkey now and theres so many to choose from its quite confusing lol

The two data cables will be fine, when installing motorised cameras we used this type of cable where power and data were all contained within a single multicore, this is for analogue systems but you can get similar with LAN cables.

https://www.fscables.com/products/rg59-composite-coaxial-cable.html
thanks. do you mean the cat5e and the analogue cable will be fine together. Have you aswell any good reccomendations for CAT 5e cable to go underground inside conduit and be pinned externally to side of house unitll fed inside. There seems to be soo much to choose from im not sure which one to get. Thanks
 
Well to narrow it down, you do not need armoured CAT cable, but you do want a cable that is rated for external use and is often referred to as weatherproof. This cable will only be weatherproof if you fit suitable glands at each end though to prevent any ingress of moisture etc.

The protection will be afforded by the conduit and there are no safety issues as with power cables. I used to use cable made by Huber & Suhner but you don't need such large rolls or that spec, try External SHIELDED CAT5e Outdoor COPPER Ethernet Cable FTP Reel 100m

Avoid cable with a CCA designation, as far as I am aware it is still not fully approved for networking, only solid or stranded copper is, cca is aluminium with a copper coating.
 
I would use 40 or 50mm white solvent weld pipe with gentle bends formed using 45 degree bends with a short bit of pipe to lessen the angle for one or two runs for cctv/data/alarm etc rather than blue pipe.

someone digging in the future will be more likely to be careful if they find a white pipe in the ground

and as spectris says AVOID cca cable
 
Thanks for the link. The 100m was out of stock so I have bought 2 of the 50m reels. Should be adequate for the runs I need. Thanks again for the info. Much appreciated.
I would use 40 or 50mm white solvent weld pipe with gentle bends formed using 45 degree bends with a short bit of pipe to lessen the angle for one or two runs for cctv/data/alarm etc rather than blue pipe.
Ill give this a look thanks. The only probelm is that part of my underground path is about a 70mm gap between my garage and a patio rite outside the back entrance. Didnt think to lay ducting when I did the patio (slightly regretting that now lol) So I havent really got much room to play with there and that is where the armoured mains cable is aswell. Plus cant be bothered to take up a row of flags and relay them again. If it will fit then I may go for it but got a few bends to deal with so like you said will have to have 45 joints in there but ive been told one whole length is better than having joins especially when underground as to keeping it water tight. Thanks again for the info much appreciated.
 
I like this idea. Just checked 50m for £35 from screwfix. Should be plenty to do three runs. I may carry on the runs into the walls at that length too lol. What is the inside diamter of the 25mm mdpe water pipe though. Do you know? Thanks

You can also get MDPE in black which is the normal colour for conduit, I'd also add a caution yellow buried electric tape over the top. MDPE is fairly tough though, it's designed to be buried, I don't believe 40/50mm solvent waste is.

It's just over 20mm inside diameter, I easily fitted 3 x cat 5 cables down without problem.
 
Many of the Swanns do have IR illumination, but there is nothing stopping you adding an external IR illuminator near the camera (indeed as many crims use a mobile to 'look' for the IR leds on the camera, you can actually 'steer' them into looking at the camera by using a separate IR illuminator on say one side of a gate or alleyway, and the camera on the other- they 'look away' from the 'camera' (thinking the illuminator is the camera) and instead end up looking directly into the actual camera (with no IR LEDs LOL)
Screenshot from 2022-01-03 15-18-04.png

I used several of these to illuminate the full length of my driveway because the cameras inbuilt ones didn't have the range to cover it fully, and being IR, they don't 'light up' like normal spotlights would

The inbuilt power cable in the 'all in one' video leads really struggles to go past 100ft/30m in my experience (it really is tiny wires inside) but you can easily run a heavier DC power cable alongside the video cable and use that instead...
(my driveway one is 500m long and although the power cable was far too weak, the supplied video plus power was fine at that distance for the video signal

I didn't use exterior grade cables, just put it in UV resistant 'flexible split duit' used on trailer wiring etc and it's hung from tree to tree down the driveway about 20ft up the gum trees lol
 